Setup Guide for the Heat Core HS05 Boiler / Air Heating hybrid unit:
Please familiarize yourself with the manufacturer’s documentation before proceeding.
HS05 + M64 Home Bitcoin Mining Heater Setup Guide
Introduction
The Heat Core HS05 combined with the WhatsMiner M64 is a compact, high-efficiency Bitcoin mining system that doubles as a home heater. Designed by HeatCore in collaboration with WhatsMiner, this 5kW unit (up to 17 MBH) captures mining heat for hot water (liquid heating) or hot air (via dry cooler), or both in hybrid mode. It prioritizes liquid heat extraction through the brazed plate heat exchanger, with excess heat vented via the DC05 dry cooler fans if needed. This ensures the miner stays cool (inlet water up to 70°C in high-performance mode) while providing eco-friendly heating.
Key Specifications (HS05 Rack):
-
Dimensions: 480mm x 600mm x 545mm (1.57’ x 1.97’ x 1.79’)
-
Weight: 35kg net / 50kg operational (including coolant)
-
Power: Max 6kW total, 5kW for miner; 200-240V single-phase, max 30A
-
Cooling Capacity: 5kW via dry cooler (4 EC fans)
-
Internal Loop: Distilled water + antifreeze + corrosion inhibitor; flow 5L/min; temps 55/70°C
-
External Heat Exchanger: Water; flow 5L/min; temps 45/60°C; φ12 barbed fittings
-
Max Pressure: Internal 4 bar, external 10 bar
Key Specifications (M64 Miner):
-
Hashrate: 180-206 TH/s (±5%)
-
Efficiency: 19.9 J/TH (±5%)
-
Power Draw: 5kW input
-
Dimensions: 371mm x 290mm x 109mm (with handle)
-
Weight: 16kg
-
Coolant: ~1L (pure water + inhibitor + antifreeze)
-
Inlet Temp: 35-55°C normal mode, 35-70°C high-performance
-
Flow: ≥3.5L/min (±10% accuracy)
-
Max Pressure: ≤400 kPa
-
pH: 6-8
-
Connections: Ethernet, custom power cable (≥25A)
Before You Start:
-
Required: Dedicated 240V/30A circuit, Ethernet/Wi-Fi, distilled water, antifreeze (e.g., ethylene glycol, ratio based on local freeze point), corrosion inhibitor (consult HeatCore).
-
Tools/Materials: Plumbing fittings (φ12 barbed), electrical tools, insulation materials, network cable.
-
Safety: Unplug before work. Use PPE. Ensure stable floor (support 50kg+). No flammable gases nearby. Check for leaks. Professional electrician/plumber recommended for wiring/plumbing.
-
Configurations: Air-only (dry cooler vents heat), Liquid-only (connect to radiant floors/hot tub), Hybrid (prioritize liquid, vent excess to air).
-
Environmental: Operating humidity 5-95% RH (non-condensing); ambient up to 35°C for design.
From “HeatCore_HS05_specs.pdf” and “WhatsMiner_M64Hydro5000w_specs.pdf”.
Unpacking and Site Preparation
-
Verify packing list: HS05 cabinet + DC05 dry cooler, main power cable, HS05-DC05 power cable, HS05-DC05 pipeline.
-
Choose location: Indoors for HS05 (e.g., basement/utility room); DC05 can detach for outdoor placement in warm weather to vent heat away.
-
Prepare site:
-
Electrical: Dedicated 200-240V/30A outlet; 3x6mm² copper cable.
-
Plumbing: For liquid mode, prepare φ12 hoses/fittings for heat exchanger.
-
Network: Ethernet cable to miner.
-
Media: Distilled water + antifreeze (30% glycol for -20°C protection; calculate via table in M64 specs) + inhibitor.
-
Foundation: Flat, stable surface; consider flood/snow impact.
-
-
Clean: Remove dust/debris from pipes with deionized water; install ≥270-mesh filter.
From “HS05_Hardware_Installation_Guide.pdf” (pages 14-15).
Liquid Heating Setup (Plumbing for Home Heating)
Connect to systems like radiant floors, hot tubs, or water heaters. Prioritizes heat to liquid; excess to air.
-
Identify heat exchanger ports on HS05 back (supply/return; labeled or per diagram).
-
Use φ12 barbed fittings; connect cold inlet (45°C design) and hot outlet (60°C).
-
Install pump/valves for circulation (rated flow 5L/min).
-
Add coolant: Mix distilled water + antifreeze + inhibitor; pH 6-8; particle size ≤53 microns.
-
Fill internal loop via reservoir (see Filling Steps below).
-
For anti-corrosion: UV sterilization, 4bar relief valve, expansion tank.
-
Test pressure: ≤400kPa internal; avoid >400kPa to prevent deformation/leaks.
-
Configurations:
-
Standalone: Loop to home system.
-
Integrated: Tie into boiler (ensure compatibility; consult plumber).
-
With pump control: Smart thermostat to circulate only when heat needed.
-
Example: For radiant floors, connect in series; monitor temp difference (close to 15°C normal, 20°C high-perf).
From “HeatCore_HS05_specs.pdf” (page 6) and “WhatsMiner_M64Hydro5000w_specs.pdf” (pages 2-3).
Air Heating Setup (Dry Cooler Configuration)
Vents heat via DC05 fans; ideal for space heating or exhaust.
-
Attach DC05 to HS05 (default) or detach for outdoor/remote placement (use provided long cables/pipes).
-
Position: Secure outdoors if detached (e.g., wall-mounted); ensure airflow unobstructed.
-
Connect power/pipeline between HS05 and DC05.
-
Fans auto-activate if liquid can’t absorb all heat (e.g., miner inlet > set-point).
-
For indoor heating: Place in target room; no ducting needed, but optional for distribution.
-
Summer tip: Detach DC05 outdoors to avoid indoor heat buildup.
Note: All heat vents here if no liquid connected; monitor room temp.
From “HS05_Hardware_Installation_Guide.pdf” (page 16).
Electrical and Network Setup
-
Power Wiring:
-
Connect main power cable to 240V/30A outlet (lug end to supply, plug to HS05).
-
Connect HS05-DC05 power (short for attached, long for detached).
-
Connect miner power (pre-fabricated cable).
-
-
Networking:
-
Plug Ethernet into miner RJ45 for config.
-
For remote temp control: Connect to HS05 RJ45.
-
Use CAT5E+ cable; dedicated 50Mbps+ bandwidth.
-
-
Grounding: Professional installation; lightning protection if needed.
From “HS05_Hardware_Installation_Guide.pdf” (page 17).
Filling and Initial Power-Up
-
Pre-Checks: See commissioning table (e.g., PPE, docs updated, clean install, secure connections).
-
Fill Coolant:
-
Unscrew reservoir cap; pour mix to max level.
-
Turn on pump; add more if level drops below 1/3.
-
Tighten cap when stable.
-
-
Power On:
-
Energize socket.
-
Switch main breaker on panel.
-
Start pump once full.
-
Miner lights/indicators should activate.
-
-
Allow 5-10 min boot; check for leaks/noise.
From “HS05_Hardware_Installation_Guide.pdf” (pages 18-19).
Miner Configuration
-
Install Miner: Place M64 in HS05 rack; connect per “MINING CONFIGURATION MANUAL” (refer to WhatsMiner docs for details).
-
Find IP: Use IP report button + scanner (e.g., Advanced IP Scanner).
-
Access Dashboard: Enter IP in browser; set pools, wallet.
-
Firmware: Optional Braiins OS for advanced controls.
-
Quick Start: Refer to “QUICK STARTUP GUIDELINE” for basics.
From “HS05_Hardware_Installation_Guide.pdf” (page 20) and original user guide.
Temperature Settings and Operation Modes
Use built-in thermostat (KCMR series) on control panel.
-
PV (top): Current temp.
-
SV (bottom): Set-point.
-
Indicators: ALM (alarm), A-T (auto-tune), OUT (control active).
Adjust:
-
Short press SET: Change SV.
-
Long press SET: Parameter mode.
-
Use shift/decrement/increment keys.
Modes:
-
Liquid Only: Connect exchanger; if saturated (e.g., hot tub full), fans activate.
-
Air Only: No liquid; all heat to DC05 fans (modulate to keep < set-point).
-
Hybrid: Liquid first; excess to air. Control via pump/smart home (off = air default).
Set inlet to 35-70°C; auto-fan if exceeded. Replace coolant yearly.
From “HS05_Hardware_Installation_Guide.pdf” (page 21) and “WhatsMiner_M64Hydro5000w_specs.pdf” (page 2).
Troubleshooting and Maintenance
-
Overheating: Check flow (≥3.5L/min), clean filters, lower set-point.
-
No Heat: Verify power, mining active, coolant level.
-
Leaks: Tighten fittings; check pressure.
-
Network: Restart, check cables.
-
Noise: Secure unit; normal fan operation.
-
Maintenance: Quarterly clean fins/filter; test coolant (per Table 4 in M64 specs); UV sterilize.
For additional support, contact us at: support@exergyheat.com